4 Wire or 5 Wire Thermostat Wiring Problem - Wifi Tstat (2024)

by High Performance HVAC | Thermostats | 13 comments

Table of Contents

4 Wire or 5 Wire Thermostat Wiring Problem - Question: We have a 19-year-old condo with an old Carrier mercury thermostat. We have both a natural gas furnace and an AC unit. There are only four wires going into the existing thermostat - red, green, blue, white. On the back of the thermostat are a number of labeled contacts, only the following have wires connecting them:
W - white wire
Y - blue wire
R - red wire
G - green wire
Y wire jumpered to a contact labeled 1

4 Wire or 5 Wire Thermostat Wiring Problem with an Air Conditioner and Gas Furnace

4 Wire or 5 Wire Thermostat Wiring Problem - Wifi Tstat (1)

Wiring in the New Base Plate for thethermostat. This is a 2 wire thermostat for heating only.

We were given a new Honeywell VisionPRO Wi-FI Programmable Thermostat model TH8320WF and would like to install it. We do not have a heat pump, so I planned to use the conventional wiring. It just seems like one wire is missing, and I suppose that is what the jumper was for on the old thermostat.
I can upload pictures if it’s helpful.

Any suggestions on how to wire the new thermostat?

4 Wire or 5 Wire Thermostat Wiring Problem - The Answer

Answer: Thanks for the email, Ed, and I’m glad to help.

The first thing we need to do is to identify the wires and where they go using our comprehensive guide to thermostat wire colors and codes.

Understanding where the wires go and what they do help you. However, color is key in most thermostat installations provided the installer followed the conventional color code.

  1. W - white wire - this wire goes to the gas controls to engage the heat on a call for heat from the thermostat when you have it set to heating mode. That closes the 24-volt control side of the gas furnace and begins the process of starting the gas furnace into its sequence of operation.
  2. Y - blue wire –This wire goes to your air conditioner and starts the air conditioner into its sequence of operation. Typically in most HVAC systems, this would be the yellow wire.
  3. R - red wire –Red is the 24-volt hotwire which would power the relays or circuit boards for the air conditioner, the gas furnace, and the blower along with any accessories in the system controlled by the thermostat.
  4. G - green wire –The G terminal or green wire goes to the blower fan inside the air handler or gas furnace to engage the blow when you turn the thermostat to the fan only.
  5. Y - wired to a contact labeled 1 - This is a mystery and without further information, I can’t tell you.

What Color Wires Go Where | 4 Wire or 5 Wire Thermostat Wiring Problem

I can only assume it is unused for anything, at least this jumper you are talking about here. On your new thermostat, you will not have to worry about this. Just follow the instructions that come with the new thermostat. That’s good news. And now, the not-so-good news. You did not mention if you had any additional wires there in the thermostat bundle because, with your new thermostat, you are going to need one extra wire.

Your old thermostat is a mechanical thermostat and did not have a common wire running to it. For the new thermostat to work, you need a 24 volt common to complete the circuit with the 24-volt hot wire to provide power for the thermostat because it is a state-of-the-art digital programmable wi-fi thermostat it will need 24-volt power to work. That means you need a 24-volt hot and a 24-volt common wire.

You already have the 24 volt hot with the red wire, so now you need to either find another wire in that bundle or run all new thermostat wire so you will have the proper amount of wires for the job.

Old Wiring - Additional Resources | 4 Wire or 5 Wire Thermostat Wiring Problem

This article will help you –Running New Thermostat Wirealong with this article - All About Thermostat Wireand another article will help you gain some understanding of basic control circuits in HVAC if you want to learn more and take it that far. Most people do not, and they end up calling in a professional to get the job done.

Wiring Chart for Basic Thermostat Wiring Terminals and Designations

4 Wire or 5 Wire Thermostat Wiring Problem
Wire Color or DesignationControl Point/Function in Equipment
W-wire - white wirethis wire goes to the gas controls to engage the heat on a call for heat from the thermostat when you have it set to heating mode. This closes the 24-volt control side of the gas furnace and begins the process of starting the gas furnace into its sequence of operation
Y-wire - yellow wire typical colorThis wire goes to your air conditioner and starts the air conditioner into its sequence of operation. Typically in most HVAC systems, this would be the yellow wire.
R-wire - red wire (can also be RH or RC - read thermostat manufacturer instructions)Red is the 24-volt hot wire which would power the relays or circuit boards for the air conditioner, the gas furnace, and the blower along with any accessories in the system controlled by the thermostat.
G-wire - green wireThe G terminal or green wire goes to the blower fan inside the air handler or gas furnace to engage the blow when you turn the thermostat to fan only.
C-Wire - Various colors but could be blue or blackThis goes to the 24 volt common side of the transoformer and is typically not used for mercusry type thermostat unless the thermostat requires power. See the thermostat manufacturers instructions.
O-wire - Orange wireThis wire is used only for heat pumps. It controls the reversing valve inside the heat pump condensing unit. Note: On Rheem and Ruud heat pumps this wire may be a different color.

4 Wire or 5 Wire Thermostat Wiring Problem - Wifi Tstat (2)

4 Wire or 5 Wire Thermostat Wiring Problem

4 Wire or 5 Wire Thermostat Wiring Problem - Additional reader frequently asked questions:

What are the 5 wire thermostats?

A thermostat with five wires typically controls an air conditioner with a heating system. The heating system will likely be a gas or electric furnace. The thermostat is likely a digital thermostat that requires the C-Wire or the common wire to provide power for the thermostat. Many newer thermostats require power, unlike older thermostats, which likely did not require power.

These were the older mercury switch thermostats that were mechanical. Mechanical versus newer thermostats that are digital. Some systems still have the older mechanical thermostats, which are typically 4-wire thermostats that control the same type of system described above.

How many wires does a thermostat need?

The answer to the question depends on the type of system you have and what kind of thermostat you have for control. Mechanical mercury switch thermostats with no special lights do not require the C-Wire. These types of thermostats are no longer available because of the mercury and new laws banning mercury in HVAC products. Here is a breakdown for mechanical thermostats and the types of HVAC systems they control:

  • Air conditioner with a gas furnace - 4-wires for single-stage and 5-wires for two-stage
  • Air conditioner with an electric furnace - 4-wires for single-stage and 5-wires for two-stage
  • Stand-alone heating systems only (gas or electric) - 2 wires*
  • Heat pump - this type of system can have up to 7 wires depending on setup

Digital thermostats normally require a power source unless they have a battery backup. For the same type of systems, here is a breakdown for the type of HVAC systems they control:

  • Air conditioner with a gas furnace - 5-wires for single-stage and 6 wires for two-stage
  • Air conditioner with an electric furnace - 5-wires and 6 wires for two-stage
  • Stand-alone heating systems only (gas or electric) - 3 wires*
  • Heat pump - this type of system can have up to 8 wires depending on setup

*Some boiler systems have multiple zones. Multiple zones require a thermostat for each zone unless you have a digital thermostat system that has linking capabilities for wireless sensors.

Use our handy calculator to see how many BTU's your natural gas appliances are producing:

COVID 19 Home Protection

UVC Light to Kill Viruses and Other Airborne Harmful Things that Affect Health

For additional protection, you can also use UV Light that will kill harmful viruses and bacteria inside the airflow of the air handler. In labs, researchers used a spectrum of ultraviolet light called UVC to kill viruses. This product requires professional installation so it will turn on and off with the blower fan in your air handler but it will offer the protection you need for you and your family from any viruses.

Click the image to the right for purchase options of the UV light to protect your family.

4 Wire or 5 Wire Thermostat Wiring Problem - Wifi Tstat (3)

Related

  1. 4 Wire or 5 Wire Thermostat Wiring Problem - Wifi Tstat (4)

    George Castilloon October 9, 2022 at 9:55 pm

    Good evening!!! Hi Fellows!!! could someone provide me a complete wiring circuit diagram with the interconnection, between Condenser unit, indoor unit and thermostat in a Lennox HS29180-240 3ph?
    I really appreciate the favor!!!
    Thanks!!!

    Reply

  2. 4 Wire or 5 Wire Thermostat Wiring Problem - Wifi Tstat (5)

    Vicki Hallon October 31, 2020 at 12:04 pm

    I currently have a programmable thermostat with 5 wires. We purchased a new basic thermostat that only has hookups for 4 wires. What do I do with the extra wire?

    Reply

    • 4 Wire or 5 Wire Thermostat Wiring Problem - Wifi Tstat (6)

      High Performance HVACon November 2, 2020 at 8:10 pm

      Use electrical tape and cover the metal part with the tape. You could also use a small wire nut with electrical tape.

      Reply

  3. 4 Wire or 5 Wire Thermostat Wiring Problem - Wifi Tstat (7)

    Paton October 5, 2020 at 3:27 pm

    I have a four wire system! I’m trying to put in new thermostat! I have a white, red, green, and blue wire but no yellow ! The blue wire was hooked up into the yellow spot! What do I need to do I thought blue was there c wire?

    Reply

    • 4 Wire or 5 Wire Thermostat Wiring Problem - Wifi Tstat (8)

      High Performance HVACon October 8, 2020 at 2:27 am

      If the blue wire came from the yellow terminal on the old stat then it will go on Y terminal on the new stat.

      For the C wire you will need an additional wire. If it is not there then you will need to pull new wire and rewire.

      Reply

  4. 4 Wire or 5 Wire Thermostat Wiring Problem - Wifi Tstat (9)

    Sajon May 17, 2019 at 5:04 pm

    In my HVAC there is no connection in Y terminal. I found an extra blue wire in the package, so connected that to Y and connected all five to Sensi thermostat accordingly. But my Ac compressor not kicking on. But Heater works fine.
    What should be done ? Please help.

    Reply

    • 4 Wire or 5 Wire Thermostat Wiring Problem - Wifi Tstat (10)

      High Performance HVACon May 18, 2019 at 11:49 am

      Without the Y control wire the AC won’t work. I advise calling a pro.

      Reply

  5. 4 Wire or 5 Wire Thermostat Wiring Problem - Wifi Tstat (11)

    Donald W Coxon November 5, 2018 at 6:21 pm

    My existing thermostat has the typical 4 wires (R, G, Y, W) but the bundle in the wall has 5 unused wires The HVAC has the same 4 wires connected and the bundle at that point has the same unused wired. On the HVAC, there is a 5th wire, which is white and connects to the C terminal. This wire, along with a red wire, go from the HVAC to the outside unit. My question is can I hook up one of the extra wires to the C terminal on the HVAC where the white wire is and then hook the other end to the C terminal on the thermostat? I need a C wire to install a new wifi thermostat.

    Reply

    • 4 Wire or 5 Wire Thermostat Wiring Problem - Wifi Tstat (12)

      High Performance HVACon November 24, 2018 at 2:38 am

      Yes, you need an extra wire in the bundle going to the thermostat. Just take the extra wire (if you have one) and attached it to the C terminal in the air handler and the other end of that same wire will go to the C terminal on the new thermostat.

      Reply

  6. 4 Wire or 5 Wire Thermostat Wiring Problem - Wifi Tstat (13)

    Normon February 23, 2018 at 10:57 am

    Question – I have five wires at the furnace. However, at the thermostat, I have only four. The two green wires at the thermostat are connected G-green, G-yellow. Why

    Reply

    • 4 Wire or 5 Wire Thermostat Wiring Problem - Wifi Tstat (14)

      High Performance HVACon February 23, 2018 at 1:09 pm

      Not sure as two greens in a bundle of thermostat wire are not normal. You will likely have to trace the wires from the source inside the air handler. Either that or call a professional to figure it and to be safe. There is high voltage inside the unit so if you do proceed to do it yourself make sure you turn the power off before proceeding.

      Reply

  7. 4 Wire or 5 Wire Thermostat Wiring Problem - Wifi Tstat (15)

    jeff levyon November 11, 2017 at 2:50 am

    HAVE A 4 WIRE THERMOSTAT FOR A 2 WIRE OUTLET. 2 BLACK 2 RED.SHOULD I JOIN THE 2 BLACKS AND 2 REDS BEFORE CONNECTING TO HOUSE POWER?

    Reply

    • 4 Wire or 5 Wire Thermostat Wiring Problem - Wifi Tstat (16)

      High Performance HVACon November 11, 2017 at 3:02 pm

      Not enough information. Upload a photo and more info……………..our uploader link is in the menu on the right.

      Reply

Submit a Comment

4 Wire or 5 Wire Thermostat Wiring Problem - Wifi Tstat (2024)
Top Articles
Latest Posts
Article information

Author: Jerrold Considine

Last Updated:

Views: 6279

Rating: 4.8 / 5 (78 voted)

Reviews: 93% of readers found this page helpful

Author information